Re: melted wires
[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: melted wires
- From: "jtrealtywebspannet" <jtrealty@xxxx>
- Date: Fri, 12 Jul 2002 14:45:36 -0000
On the surface your suggestion of fusing the ground makes some sense
until you consider what happens after the fuse blows. Because the
ground is "daisy chained", ie, the grounds are point to point with one
finally ending up at true ground, by fusing it and having it blow will
create a backfeed through the other circuits. Also consider that the
size of the grounding fuse must be capable of ALL loads daisy chained
into it so it carries more than just 1 circuit's return current. If
you have a ground wire melting you have bigger problems than what can
be "fixed" with a fuse. A better solution would be to ground both ends
of the daisy chain. The fuse that supplies each circuit is meant to
also protect the return portion of the circuit also. Make sure EVERY
fuse is the correct size for it's position. Even though the wiring
of each individual circuit may be capable of carrying more current
than the fuse is sized for you can see from this scenario that the
grounds must carry the cumulative total of all the circuits so any
oversized fuses will allow excess current into the ground.
Having backfeeds into other circuits can cause you to pull your hair
out trying to figure out what is going on. This can be one of the
hardest things to diagnose and repair so setting things up to fail in
this mode is not a good idea.
David Teitelbaum
vin 10757
--- In dmcnews@xxxx, dherv10@xxxx wrote:
> Shain, That's a good idea, but it all circles back to one ground
wire. No
> matter how you get there, it's one ground back. If you really want
to help
> the situation, then fuse the ground wire. That way if you have a
short that
> one fuse in the box doesn't catch it, the ground fuse might.
> John Hervey
> http://www.specialtauto.com/
>
>